Hello,
I have a 4-20mA HART valve positioner in the field that is controlled via the DCS (analog output card) connected with a #16 2 wire cable.
I have intermittently Not Communicating With Device alarms at the DCS. Which means the HART signal goes away.
When I check resistance between earth ground and the negative terminal at the device, I notice resistance up to 80Kiloohms, so maybe floating ground. :?
Any suggestions or recommendations.
Thank you
I have a 4-20mA HART valve positioner in the field that is controlled via the DCS (analog output card) connected with a #16 2 wire cable.
I have intermittently Not Communicating With Device alarms at the DCS. Which means the HART signal goes away.
- I put an oscilloscope on the wire and saw voltage spikes up to 9V.
- We check the cable and it is good.
- Valve specialist came and inspected the valve and checked out good. The specialist
- The shield is terminated to references ground back that DCS cabinet. and the shield is not terminated back at the device.
- I check for noise on similar valve in a different area and I saw small noise of about 1V spike and this valve works perfectly good with no communication issues.
- The problem valve is located next to 2 VFD medium voltage pumps, so I suspect this AC voltage could be causing noise.
When I check resistance between earth ground and the negative terminal at the device, I notice resistance up to 80Kiloohms, so maybe floating ground. :?
Any suggestions or recommendations.
Thank you