monkey_man_100
Member
Where is the c mils of Nmb (romex)? I am trying to figure out how many 14-2 conductors I can run through a 1-1/2'' hole.
infinity said:You can stuff in as many as will fit. If they're bundled for more than 24" then derating will apply. Bundling wouldn't apply to the portion within the hole unless it was sealed with a draft or fire stopping compound.
How about 334.80 the last paragraph.:smile:tallgirl said:Is there a code section for that, because I'd like to propose that that is a stupid code section and needs to be tossed.
rlMutch said:How about 334.80 the last paragraph.:smile:
I agree with the tossing comment.
tallgirl said:And the handbook says it's new for '05 stupidity.
Bob NH said:The rating for 90 C conductors in NM B is 30 Amps for #12 and 25 Amps for #14 (Reference Table 310.16).
Derating those to 70% for 7 to 9 CCCs gives you 21 and 17.5 Amps respectively.
Since the OCPD limits of 240.4(D) for 12 and 14 AWG are 20 and 15 Amps, you can stuff four (4) pieces of 2-conductor NM B through a hole, complete with firestop foam, without having to reduce the ampacity/OCPD below 20 and 15 Amps for 12 and 14 AWG.
tallgirl said:And none of that answers the question -- is it safe if not foam sealed, but still crammed tight as can be?
310.15(2) Selection of Ampacity. Where more than one calculated or tabulated ampacity could apply for a given circuit length, the lowest value shall be used.
Exception: Where two different ampacities apply to adjacent portions of a circuit, the higher ampacity shall be permitted to be used beyond the point of transition, a distance equal to 3.0 m (10 ft) or 10 percent of the circuit length figured at the higher ampacity, whichever is less.
tallgirl said:Yeah, but what about framing members above panels where typically a zillion CCCs are passing through a small number of holes on their way into the attic?
That practice has been going on for decades. Has it been safe because residences (where most NM is used) tend to have far more circuits than capacity, or because this is one of those things that only happens under lab conditions, like drinking too much soda causes cancer?
I help rough a house this weekend that had something like 24 circuits on a 125A service. We ran 12 pieces of 12/2, more or less, through 2 Really Big Holes, both of which I'm sure will be foam sealed.
And none of that answers the question -- is it safe if not foam sealed, but still crammed tight as can be?
tom baker said:The great thing about this rule on sealing foam is that it brings out that the ampacity of 12-2 NM B is 30 amps for derating.
tallgirl said:Working that backwards gives 24 * 13.5A = 324A which is significantly greater than the service size of 125A. Which is why I said its a stupid rule. For a typical residential application there likely isn't the service capacity to create the problem. The 7 to 9 CCCs before derating reduces the ampacity to below 20A would consume enough of the service that I just don't see it happening, as I showed above.
acrwc10 said:I like the rational of your arguement.
tallgirl said:Yeah, especially since that's only HALF of the panel -- there's another 2" hole with the other 24 CCCs passing through it. The total for that situation would be 648A -- just to get up to what the Code says would be permitted IF derating were applied.
It's the same thing as those stupid rats they fed too much soda -- sure, it's possible to create problems if you can somehow get a 1200 sqft house to consume 77kVA -- which would be permissible if all 24 circuits were loaded to their derated limit of 13.5A.
Likely? Nope. The service lateral, feeder, and everything else involved would likely have long since melted. But those pieces of NMB would still be safe.
tallgirl said:Yeah, but what about framing members above panels where typically a zillion CCCs are passing through a small number of holes on their way into the attic?
That practice has been going on for decades. Has it been safe because residences (where most NM is used) tend to have far more circuits than capacity, or because this is one of those things that only happens under lab conditions, like drinking too much soda causes cancer?