Where to find this public input proposed change?
wc86
Massachusetts
Do you guys know where i can find this?
"Mike has a different proposal 3204-NFPA 70-2023 [ Section No. 220.82(B)] That would lump EVSE's under B(3) and continue to allow the EVSE to be considered in the demand factor."
That is a PI for the 2026 code. Go to www,nfpa.org/70, select next edition and then "first draft report". Note that Article 220 has become Article 120 and you will look in that new article for the section. At the top of 120,82(B) says "PIs(7)" You click on that to see the PIs that were submitted for that section.
Note that PI was rejected and a new first level subdivision (D) was added to address the ESVE loads.
(D) EVSE Loads.
The total load of an EVSE shall be calculated at 100 percent in accordance with 120.57.