Where to Place SPD to Protect Inverter/ATS?

samgillis

Member
Location
California, USA
Occupation
Electrician
So I have a Go Power 50a ATS that is fed by my inverter as the primary and grid as the backup.

The grid feed is already protected by a Siemens whole home surge protector in the main panel. Does this adequately protect the circuit board of the ATS?

I also just purchased a Midnite Solar SPD and was going to place it in the ATS, just trying to figure out where is best.

I already have surge protection on the DC side into the inverter from the panels and batteries. Would placing the new SPD on the inverter AC out and before the input to the ATS be best? Would this also provide some protection to the inverter even though it’s on the output side? Or would it be best to place it on the output side of the ATS?
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
Your inverter should be protected by the main SPD when connected by the ATS to the utility. When islanded by the ATS you may want another SPD on the inverter side of the ATS. Your inverter might already have an SPD on the AC side, but the included ones are not always the best. When you are islanding what will be the source of the voltage spike you want to prevent? That should drive the location of the SPD.
 

samgillis

Member
Location
California, USA
Occupation
Electrician
Your inverter should be protected by the main SPD when connected by the ATS to the utility. When islanded by the ATS you may want another SPD on the inverter side of the ATS. Your inverter might already have an SPD on the AC side, but the included ones are not always the best. When you are islanding what will be the source of the voltage spike you want to prevent? That should drive the location of the SPD.
Mostly lightning protection of the inverter and ATS is what I’m after. But I have read that the actual switching of the ATS from source 1 to source 2 creates transient voltage spikes and can damage the load equipment. So was wondering if by placing the SPD on the output of the ATS would it essentially kill 3 birds with one stone by protecting the downstream loads, ATS board, and inverter output all at once, or if my logic is flawed there should I just put it on the inverter side like you said to protect the inverter and ATS which is my main goal.
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
This "ATS" is an RV product and not suitable for use in a residential system.
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
What makes it unsuitable
I've used many "RV" products and they are just generally lower quality than the same product intended for residential use. They are designed to be used in an RV that is used a few times a year and does not get that much wear and tear.
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
Also, searching the ETL product listing does not return anything for this company or the product number. I'm not convinced it is listed to UL 1008.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Also, searching the ETL product listing does not return anything for this company or the product number. I'm not convinced it is listed to UL 1008.
551.30, 551.33, 551.40 all require products to be listed for the use. If there is no listing at all, it can't "legally" be used. Listing also could be limited to the RV usage, and thus technically "not listed" in other applications.
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
Seems like this is becoming a discussion on how to do an DIY solar project. Even if the person doing the DIY is a electrician it's better put in a DIY forum.
 

samgillis

Member
Location
California, USA
Occupation
Electrician
The question was about best placement of an SPD to protect an inverter and transfer switch, which I figured would warrant some good responses since this forum is compromised of electricians and engineers. What kind of ATS and whether it has anything to do with solar is irrelevant. Anyway, I figured out the answer through another means.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Surge protection devises only limit a portion of any transient spikes. Depending on how critical or sensitive your equipment or devices you are trying to protect a multi level protection is usually best, each level drops out some of the transient.
What kind of ATS and whether it has anything to do with solar is irrelevant.
Not irrelevant or unimportant and this is primary reason DIY question is not considered here. Many factors come into play that would effect potential application of any "advise" given that will "change everything" if was to be known.

The suggestions that specific equipment or installation procedure is being done that would be a violation of code or might be a hazardous installation, should always be called out by an "electrician", and welcomed by an "electrician" resulting from suggested procedure or equipment is an "OOPS, I missed that".
 