What is the best location for lightning protection "test well"? At the corner of the building? Or does it need to be close to the main electrical room? Thanks.
The grounding test wells I have worked with had a mechanical connection to the electrode so that you could test the ground resistance of the electrode itself.Here's one of two we installed on the grounding ring at an outdoor cell site.
I think it's so they could test the impedance with a clamp-on ground tester.
View attachment 2555500
Here's one of two we installed on the grounding ring at an outdoor cell site.
I think it's so they could test the impedance with a clamp-on ground tester.
I suggest putting it where you will get the worst case readings.
Depends on what type of lightning protection system installed, Catenary, Integral, or Mast-Type. Test wells are usually required when the system electrodes or ground loop are required to be tested. Test wells are used so that the driven electrode can be isolated from the rest of the system. Some systems; systems without a ground loop have a down conductor that attaches directly to the driven electrode. NFPA 780 says that the down conductor "shall be attached permanently to the grounding electrode system by bolting, brazing, welding, or high-compression connectors listed for the purpose".What is the best location for lightning protection "test well"? At the corner of the building? Or does it need to be close to the main electrical room? Thanks.
Still the overall ground resistance of the lightning protection system may be measured and compared with the standard value, if any.It would seem to me if the connections were all permanent (brazed, welded) the test well would be useless except for knowing where your driven electrodes were located.