Previous thread was about 225.10 NEC 2014 however this one about which one applies.
What I have is UF cable outside and installers are saying quoted one of the wiring methods of NEC 2014 225.10 but even with that UF cable is subject to physical damage. NEC 2014 section 225.10 has shall be permitted wording. However, NEC 2014 section 340.12(10) prohibits it from using UF cable due to physical damage but 225.10 says cannot prohibit it shall be permitted. Installers are saying 225.10 cannot be rejected. Not sure which would apply 340.12(10) or 225.10?
What I have is UF cable outside and installers are saying quoted one of the wiring methods of NEC 2014 225.10 but even with that UF cable is subject to physical damage. NEC 2014 section 225.10 has shall be permitted wording. However, NEC 2014 section 340.12(10) prohibits it from using UF cable due to physical damage but 225.10 says cannot prohibit it shall be permitted. Installers are saying 225.10 cannot be rejected. Not sure which would apply 340.12(10) or 225.10?