We are talking past and present. If a breaker is UL listed today it negates past requirements.
Sent from my SM-T350 using Tapatalk
+1Huh?
CLASSIFIED MOLDED CASE CIRCUIT BREAKERS FOR USE IN SPECIFIED EQUIPMENT
97. Classified Only and Compatibility List - A circuit breaker that is Classified only is marked on the side with the statement:
"Classified for use only in specified panelboards where the available short-circuit current is 10 kA,
120/240 volts ac or less. Do not use in equipment connected to circuits having an available system short-circuit current in excess of 10 kA, 120/240 volts ac. For catalog numbers (or equivalent) of
specified panelboards, refer to Publication No. provided with this circuit breaker. If additional information is necessary, contact [Classified circuit breaker manufacturer's name]."
98. Classified and Listed Compatibility List - A circuit breaker that is both Classified and
Listed is marked on the side with the statement:
"This circuit breaker is Listed for use in circuit breaker enclosures and panelboards intended and marked for its use. This circuit breaker is Classified for use, where the available short-circuit current is 10 kA, 120/240 V ac or less, in the compatible panelboards shown in Publication No. provided with this circuit breaker. When used as a Classified circuit breaker, do not use in equipment connected to circuits having an available system short-circuit current in excess of 10 kA,
120/240 V ac. If additional information is necessary, contact [Classified circuit breaker manufacturer's name]."
99. Compatibility List - The referenced publication is a compatibility list which tabulates the company name, catalog number, number of poles and electrical ratings of the Classified circuit breaker, in addition to the company name and catalog number of the applicable UL Listed panelboards, and corresponding UL Listed circuit breakers in place of which the Classified circuit breaker has been investigated. The compatibility list also details the maximum permissible voltage and maximum available short circuit current of the supply system to the panelboard. The Classified circuit breaker is not suitable for the specified application if the system supply characteristics exceed the maximum values indicated in the compatibility list. One copy of the compatibility list is provided with each circuit breaker.
100. Classification and Listing Mark - Circuit breakers that are both Classified and Listed have markings as above, with the addition of the Listing Mark, located on the side of the circuit breaker.
The following mark: appears on the front, visible surface of the circuit breaker.
101. General Markings- These circuit breakers are also marked as outlined for all breakers. See items 1-7,14-21, 39-40, 42-43, 51-66 and 89-96.
Correct!To rephrase, possibly:
If, at the time of manufacture, a certain list of breakers was compatible, then if since that time additional breakers are listed by UL as replacements for any of the breakers on that list, the list should be considered expanded.
Similarly if the manufacturer's name for a breaker on the list is changed but the breaker remains identical, that newly named breaker should be considered as compliant with the list.
However, there does not appear to be any explicit NEC or UL language to that effect.
One more note: If the manufacturer adds to the compatible list, but does not re-issue and retrofit the existing compatibility labels, the new list should still apply.
Sorry, but I do not agree with this assessment. The breaker is furnished with a compatibility list at the time of manufacture. You cannot assume anything beyond what is on that compatibility list that comes with the breaker because it has not been investigated. See item 99 in the excerpt I quoted above.To rephrase, possibly:
If, at the time of manufacture, a certain list of breakers was compatible, then if since that time additional breakers are listed by UL as replacements for any of the breakers on that list, the list should be considered expanded.
Similarly if the manufacturer's name for a breaker on the list is changed but the breaker remains identical, that newly named breaker should be considered as compliant with the list.
However, there does not appear to be any explicit NEC or UL language to that effect.
One more note: If the manufacturer adds to the compatible list, but does not re-issue and retrofit the existing compatibility labels, the new list should still apply.
I was referring to overriding the list provided with the *panel* at time of manufacture.Sorry, but I do not agree with this assessment. The breaker is furnished with a compatibility list at the time of manufacture. You cannot assume anything beyond what is on that compatibility list that comes with the breaker because it has not been investigated. See item 99 in the excerpt I quoted above.
The panel list in 1985 is irrelevant to a UL listing of 2017I was referring to overriding the list provided with the *panel* at time of manufacture.
I agree that the compatibility of the breaker is final as of the time of manufacture.
Limiting though it may be, an old model of a compatible breaker could not take advantage of an later expanded list for an identical breaker.
Sent from my XT1585 using Tapatalk
What compatibility list is furnished with and for a panelboard? If there is one furnished with a panelboard, it is for one or more breakers that come with the panelboard.I was referring to overriding the list provided with the *panel* at time of manufacture.
I agree that the compatibility of the breaker is final as of the time of manufacture.
Limiting though it may be, an old model of a compatible breaker could not take advantage of an later expanded list for an identical breaker.
Sent from my XT1585 using Tapatalk
What compatibility list is furnished with and for a panelboard? If there is one furnished with a panelboard, it is for one or more breakers that come with the panelboard.