Which column in 310.16 for Romex ?

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
Please help me remember, which ampacity column do I use for romex cable? 75 degree? 60 degree? column for individual conductors ran in conduit? That’s different if I remember. Thank you !
 
NM is rated 60C although their are 90C conductors in the cable. You can use 90C for de-rating buit the final overcurrent protective device cannot be more than the 60C column
 