sparkyguy545
Using IEEE-1584, if you have a 2000 A MCB switchboard, do you utilize the instantaneous trip time for the MCB in the switchboard to calculate the PPE label, or are you required to use the upstream device (feeder) trip time? At a recent seminar, I've heard that you must use the upstream device ONLY due to the fact that the line-side of the MCB could be flashed. OK, this is the safest condition since the line-side of the MCB could flash. However, it makes construction difficult because SWBD's with large MCB's would be required to keep the Main CB in a separate section in order to have a lower-rated (safer PPE level) distribution section. I can also see the argument this is overly-conservative and you should utilize the MCB instantaneous trip to calculate the PPE for the eitire SWBD. I don't have the entire IEEE-1584 to refer to, so references appreciated.