which one to follow, NEC OR IEEE979 for speration distance of outdoor oil transformer?

Status
Not open for further replies.

Leo Li

Member
Location
China
Occupation
Engineer
Just check the Seperation distance between 13.2/480V outdoor oil transformer (assume oil tank is 10000L) and building non-fire wall or between two transformers, in IEEC- 979, it state as below:


IEEE-979.PNG
So From building wall to transformer or between two transformer should be 25ft .

But if follow NEC 110.34(A) table it from wall to transformer to be 6ft (condition2 for beyween transformer and wall) and 9ft (condition 3 for between two transformer) wihch is much less than requirement above IEEE979.
NEC-2020.PNG

Below is our project drawings. It meer NEC but not meet IEEE-979. so I am confused which one to be followed or my understanding is wrong?

Thanks !!!
drawings.PNG
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Those two documents address two totally different things. The NEC is only looking at having enough space to safely work on the equipment. The IEEE document is looking at fire issues. Those are not in the NEC, but may be in the building or fire code that applies to the installation.
 

Leo Li

Member
Location
China
Occupation
Engineer
Those two documents address two totally different things. The NEC is only looking at having enough space to safely work on the equipment. The IEEE document is looking at fire issues. Those are not in the NEC, but may be in the building or fire code that applies to the installation.
thanks!
 