Re: Which Table?
Pierre,
to be safe, I would use 310.16.
That said, 100 out of 100 that I've ever seen were wired using 310.15(B)(6).
Now if you want some fun reading from some older threads, check these out:
.15(B)(6) or .16 #1
.15(B)(6) or .16 #2
.15(B)(6) or .16 #3
.15(B)(6) or .16 #4
.15(B)(6) or .16 #5
How many remember this from the last link:
The following is from an old thread, substitute your numbers as applicable.
quote:
This article specifically allows reduction to the first lighting appliance
branch-circuit panel(s) down line of the service equipment.
We will use a lateral in this example
400A service
2-200 amp lighting appliance branch-circuit panels.
Service lateral --400KCM copper per article 310.15(b)(6) to 400A OCPD.
We still have not made it to our lighting appliance branch-circuit panels
yet.
For sake of conversation we install 2-200 amp enclosed breakers adjacent to
this 400 amp OCPD and feed these from parallel lugs.
We use 2/0 copper per 310.15(b)(6).
We still have not made it to our lighting appliance branch-circuit panels
yet.
We feed 2-200 amp lighting appliance branch-circuit panels with 2/0 copper
per 310.15(b)(6)and make all terminations.
We have finally made it to our lighting appliance branch-circuit panels.
Now 310.15(b)(6) has seen it's end and if we feed any sub panel, say a 100
amp, from one of these aforementioned lighting appliance branch-circuit
panels, this 100 amp sub panel can not use 310.15(b)(6)