Paul the BIG Finn
Member
- Location
- Ashburn, VA
We requested a 3,000A, 480V delta service from the utility for a large industrial user. The utility service told the contractor they could not connect the green ground wires that had been pulled with the power conductors and also the ground conductors would have to be removed before they would connect the power conductors. They assured the contractor and only the power conductors were required for a delta service.
When the electrical inspector came to the site for final inspection he told the contractor that because the utility had installed a delta/wye transformer we would need a neutral connection, even though there was no neutral distribution in the building. In his opinion the ground fault relays on the service would not not have a true reference point and would not function without the neutral. Since it required for reference only, i.e. there is no unbalanced load on the neutral the contractor ask it we could we run a single reference conductor. The inspector cited NEC 250.24(C)(2) which refers to NEC 250.24(C)(1) which refers to NEC 250.102(C)(1) which references Table 250.66 with the addition "the supply-side bonding jumper shall have an area not less than 12 1/2% percent of the area of the largest set of ungrounded supply conductors."
In short, they are insisting we provide a full size neutral for the service in spite of the fact there will not be any current on that neutral.
I have searched the code and can't find an exception. Does anyone have any thoughts on this other than pulling in a 600 kCMIL neutral in each of the parallel conduits?
When the electrical inspector came to the site for final inspection he told the contractor that because the utility had installed a delta/wye transformer we would need a neutral connection, even though there was no neutral distribution in the building. In his opinion the ground fault relays on the service would not not have a true reference point and would not function without the neutral. Since it required for reference only, i.e. there is no unbalanced load on the neutral the contractor ask it we could we run a single reference conductor. The inspector cited NEC 250.24(C)(2) which refers to NEC 250.24(C)(1) which refers to NEC 250.102(C)(1) which references Table 250.66 with the addition "the supply-side bonding jumper shall have an area not less than 12 1/2% percent of the area of the largest set of ungrounded supply conductors."
In short, they are insisting we provide a full size neutral for the service in spite of the fact there will not be any current on that neutral.
I have searched the code and can't find an exception. Does anyone have any thoughts on this other than pulling in a 600 kCMIL neutral in each of the parallel conduits?