jxofaltrds
Inspector Mike®
- Mike P. Columbus Ohio
- ESI, PI, RBO
Found this today. Sad to say it passed an inspection.
I thought that was a plastic frame but wasn't certain,Sorry if the picture is not clear.
The 'bond' is in the upper left of the picture. Left of the green screw.
The water clamp is attached to the 'plastic' frame.
What is the bonding conductor attached to on the other end?
If this is a hydromassage bathtub there is a good chance that there is no bonding required.
Chris
A #6 bare was run to the panel.
Specs were not on site. Since the bond was run I saw no need to ask for the specs.
I was doing the construction inspection for the buyer not acting as the AHJ.
Running a #6 bare from a hydromassage bathtub bonding lug to the panelboard is an absolute waste of time and money. 680.74 specifically states that the bonding jumper shall not be required to extend or attach to any remote panelboard.
The lug on the hydromassage bathtub is there for equipotential bonding in the area of the tub.
Chris
Agreed. My only concern was 'since' the 'bond' was there it should be connect correctly.
So as an inspector what is the code section you would cite for the violation?
Chris
If the bond isn't require (plastic water pipes) then the bonding conductor could have been left unconnected and push aside, but if there was metal piping then there should have been a bond from the proper lug on the motor to the metal piping. (680.74)
My call would be put it to the metal water pipes and call it an extra water bond, then install the proper bond to the motor.
To the correct lug of course:roll:
So if the bond was not required would 'bonding' the plastic be a violation?
Why would that be a violation Mike. It is totally crazy to think some one did this but it would take one minute to move the wire to the lug and be done with it. You cannot turn someone down for bonding plastic.So if the bond was not required would 'bonding' the plastic be a violation?