I have a situation I would like some opinions about.
A few years ago we designed and sold a machine that included a single phase 480vac - 240vac transformer used to supply a series of servo motor drives. The original design was for the 240v secondary power to be left ungrounded. As a result the wire colors were to be black.
At some point after the machine was installed, one leg of the 240v secondary was grounded. I do not know if this was done by end-user personnel or our own service personnel nor do I know why it was designed ungrounded then later grounded.
Here's my dilemma. I am now in the process of designing additional servo drives into the system using the same 240v secondary power supply. When the leg of the secondary was grounded, the newly grounded conductors were left black and therefore do not correctly identify the grounded conductor as grounded.
As part of my installation instructions for my new design, I believe I have a responsibility to order the existing grounded conductors replaced or at least marked with white tape or something to indicate that they are grounded. I do not believe the NEC would require the wire to be replaced if marked as grounded. The additional grounded conductors that will be added by my design will be ordered white.
Is this an appropriate action?
Edit: Incidentally, the ungrounded secondary conductor was originally designed and remains red. Don't think this matters but thought I'd add it.
Bob
[ December 27, 2005, 02:52 PM: Message edited by: bthielen ]
A few years ago we designed and sold a machine that included a single phase 480vac - 240vac transformer used to supply a series of servo motor drives. The original design was for the 240v secondary power to be left ungrounded. As a result the wire colors were to be black.
At some point after the machine was installed, one leg of the 240v secondary was grounded. I do not know if this was done by end-user personnel or our own service personnel nor do I know why it was designed ungrounded then later grounded.
Here's my dilemma. I am now in the process of designing additional servo drives into the system using the same 240v secondary power supply. When the leg of the secondary was grounded, the newly grounded conductors were left black and therefore do not correctly identify the grounded conductor as grounded.
As part of my installation instructions for my new design, I believe I have a responsibility to order the existing grounded conductors replaced or at least marked with white tape or something to indicate that they are grounded. I do not believe the NEC would require the wire to be replaced if marked as grounded. The additional grounded conductors that will be added by my design will be ordered white.
Is this an appropriate action?
Edit: Incidentally, the ungrounded secondary conductor was originally designed and remains red. Don't think this matters but thought I'd add it.
Bob