I was wanting to know what other people are using for multi metering that offer two CT metering for 400 amp 120/208 services?
I personally do not understand what you are asking. Are you talking about sub metering or utility metering?
Siemens always does good.
So does SqD.
Part of confusion here is that in those situations you generally don't have 2 services, technically you have one service with the up to six permitted disconnecting means. In general a building can only be supplied with one service, with some exceptions being different voltage, phase, frequency or other characteristics, and sometimes just because the capacity is larger than the utility will serve with a single service, but that is often over 2000 amps, maybe lower with single phase installations. Another problem that you have mentioned is what the POCO will supply you with as compared to what NEC will allow. Your situation of two different occupancies generally is acceptable to have separate service to each according to NEC, but apparently your POCO doesn't want to allow this.I see a lot of people out here doing 200amp services with 2 services to make a 400amp service which I guess if it was a new building or something like that its probably a more cost efficient way of doing things, but when you need a true 400 amp service this doesn't work.
Part of confusion here is that in those situations you generally don't have 2 services, technically you have one service with the up to six permitted disconnecting means. In general a building can only be supplied with one service, with some exceptions being different voltage, phase, frequency or other characteristics, and sometimes just because the capacity is larger than the utility will serve with a single service, but that is often over 2000 amps, maybe lower with single phase installations. Another problem that you have mentioned is what the POCO will supply you with as compared to what NEC will allow. Your situation of two different occupancies generally is acceptable to have separate service to each according to NEC, but apparently your POCO doesn't want to allow this.
The other thing you have is with multiple service disconnecting means, common supply conductors to both only need an ampacity equal or greater than the calculated load. What this means is even though you have 2- 400 amp overcurrent devices, if the total load calculation is only 525 amps, your common service conductors need not have an ampacity over 525 amps, but if you were to supply a single 800 amp device you would need 700 amps of conductors. (700 because of next higher standard overcurrent device rule, over 800 amps and this rule can not apply)
What the heck is a "strike"? Service drop?:?