We have a customer with a 3000A service installed by us a few years ago. They have a 500HP compressor on a softstart fed from this gear that's been blowing fuses randomly. So one day when we're in the electrical room we noticed it made a terrible vibrating-rattle like noise on startup. Scary sounding enough, that my apprentice was halfway out the door when I looked around for him.....chicken!
Had the POCO shut them down today to check all the connections. All buss connections looked great, no heat marks anywhere, but we found six 3/8 x 1" bolts LOOSE where the bussing bolts to a long fiberglass insulator. The nuts on some of them were backed off about 2 turns and they were right over the Pringle main disconnect switch. I don't even want to think what would happen if one dropped...
But, a little loctite and now they're good to go!
Unfortunately, we turned the power back on and that damn vibrating/rattle is still there. I really thought we had it. Now I'm thinking it's the sheetmetal at the back of the switchgear that I can't get to, that's causing the noise. Except for pulling the gear out to get to the back, I think the customer is going to have to live with it.
Had the POCO shut them down today to check all the connections. All buss connections looked great, no heat marks anywhere, but we found six 3/8 x 1" bolts LOOSE where the bussing bolts to a long fiberglass insulator. The nuts on some of them were backed off about 2 turns and they were right over the Pringle main disconnect switch. I don't even want to think what would happen if one dropped...
But, a little loctite and now they're good to go!
Unfortunately, we turned the power back on and that damn vibrating/rattle is still there. I really thought we had it. Now I'm thinking it's the sheetmetal at the back of the switchgear that I can't get to, that's causing the noise. Except for pulling the gear out to get to the back, I think the customer is going to have to live with it.