N nizak Senior Member Saturday at 9:54 AM #1 Correct me if my missing something. If the Emergency disconnect is shut off, won’t the generator start and provide power to the dwelling?
Correct me if my missing something. If the Emergency disconnect is shut off, won’t the generator start and provide power to the dwelling?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Saturday at 9:55 AM #2 Yep.
N nizak Senior Member Saturday at 10:08 AM #3 LarryFine said: Yep. Click to expand... Are there requirements in the code to also turn off generator power or just Utility power?
LarryFine said: Yep. Click to expand... Are there requirements in the code to also turn off generator power or just Utility power?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Saturday at 10:35 AM #4 I believe it's covered by required labeling of there being multiple sources.
Seven-Delta-FortyOne Goin’ Down In Flames........ Location Humboldt Occupation EC and GC Saturday at 11:48 AM #5 What Larry said. All the ATS i install have a label that you fill out showing where the gen is located. And the generator is required to have an external shut off switch.
What Larry said. All the ATS i install have a label that you fill out showing where the gen is located. And the generator is required to have an external shut off switch.