Bob Schuman
Member
- Location
- Hawley, Pa
Can you run back through meter base from transfer switch to refeed existing panels
Usually we just take the load side from the meter, conduit or cable , and feed the ATS, then from the ATS to the panel. So you are saying you want to nipple over the the TS from the meter and then back through to your panel. I did something similar once and it was 200 amp and wasn't easy going in and back through the 2 " conduit nipple I had put in. It was 3/0 copper so I thought it would be okay but I wouldn't do it again.So it would require two conduits, one feeding the transfer switch and one returning load feeds to existing panels. If utility co will allow
You can't return back through same nipple, unless the return is still service conductors - which if you have a listed transfer switch and follow listing - return conductors won't be service conductors.Usually we just take the load side from the meter, conduit or cable , and feed the ATS, then from the ATS to the panel. So you are saying you want to nipple over the the TS from the meter and then back through to your panel. I did something similar once and it was 200 amp and wasn't easy going in and back through the 2 " conduit nipple I had put in. It was 3/0 copper so I thought it would be okay but I wouldn't do it again.