Ok, it's a 1953 residential duplex. Lighting hit a tree in the front yard. Some of the current flowed along the metal underground water pipe to the house, through the GEC(s), and out through the system (supplemental GECs to rods, siding, one TV). Minimal known damage to utilization equipment or GFCIs.
Normally to test I'd disconnect all sensitive equipment, unscrew lamps, and test each branch individually.
For simple pass/fail results might the testing start at the load side of the meter base(s)? Specifically, is there any chance of damage to the MCBs (100 amp SqD HOMs, then normal branch circuit breakers) with a 1000v crank?
If the wiring passes that way, several hours of individual branch testing might be saved per side.
Normally to test I'd disconnect all sensitive equipment, unscrew lamps, and test each branch individually.
For simple pass/fail results might the testing start at the load side of the meter base(s)? Specifically, is there any chance of damage to the MCBs (100 amp SqD HOMs, then normal branch circuit breakers) with a 1000v crank?
If the wiring passes that way, several hours of individual branch testing might be saved per side.