I believe this was brought up before but I cant remember exactly. Does any one know why #12 was restricted to 20 amp breakers and #10 to 30 amp and # 14 to 15amp?? Im speaking of the 75 degree column of course. 
That was about the time Neher-McGrath came on the scene. Not sure if it has any bearing.Somthing happened in 1956. I don't remember it as I was just a twinkle in Daddy's eyes Momma didn't understand.
---------------------------------------------------------------
Small conductor rule (T310.16) history:
The current Table 310-16 has a rather 'mobile' history, whose lineage is as follows:
In the original 1897, ampacities were listed in a table titled Rule 16, titled "Table of Carrying Capacity of Wires". 14, 12 and 10 had ampacities of 12, 17 and 24 for rubber insulation, 16, 23, and 32 for other insulations (those were your only two choices then!).
In the 1911 NEC it was called Rule 18 and was re-titled as "Allowable Carrying Capacities of Conductors."
In 1920, it became Table 1 of Rule 18.
In 1923, it was Table I to Rule 610. This was the first of three major renumberings of the NEC
In 1930 NEC, it was relocated as Table 1 of Rule 618.
In 1937, it was moved to the back of the book and became Table 1, Chapter 9. This was the second of three major renumberings of the NEC
In 1940 Table 1 was moved further back to Chapter 10.
In 1956, the following was added to the bottom of the table:
"The current-carrying capacities for Type RHH conductors for sizes 14, 12 and 10 shall be the same as designated for Type RH conductors in this Table." This put 14, 12 and 10 at 15, 25 and 40 amps respectively.
In '59 it was relocated again and became Table 310-12. The ampacites were also changed for Type RH conductors, so this put 14, 12 and 10 at the ratings of 15, 20 and 30 amps we know today. This was the third of three major renumberings of the NEC.
In '65, the Table was renumbered 310-15.
In 1978, the 14AWG/15a, 12AWG/20a and 10AWG/30a were obelisk (?) notes at the bottom of (again renumbered) T310-16.
In 1999, the obelisk note was changed to refer to 240-3.
In 2002, the reference was changed to 240.4(D).
---------------------------------------------------------------
What happened in 1956? I have no clue.
That would defeat the purpose of derating.Does changing wire sizes for voltage drop also fall under 240.4 (D)? Example: upsizing the wire to a #10 which was previously protected by a 20A breaker. Do you have to change the breaker to a 30A?
And what if you receive a mechanical cut that says 19 MCA and 25 MOCP? Do you have to go with a #10?
That would defeat the purpose of derating.
Somthing happened in 1956. I don't remember it as I was just a twinkle in Daddy's eyes Momma didn't understand.
What happened in 1956? I have no clue.
240.4(D) answers the question: "the overcurrent protection shall not exceed the following after any correction factors for ambient temperature and number of conductors have been applied".
So you can put a 15, 20, or 30A breaker on a #10 wire, You just can't go larger unless you fit in one of the expceptions.
Hmmm. Was it spelled different back then? I found:Something very important happened...I was born.![]()
If you want NEC history, check with 480sparky. I think he has a copy of every NEC version.Where did you find this history lesson? The handbook? (Don't have mine with me)
I believe this was brought up before but I cant remember exactly. Does any one know why #12 was restricted to 20 amp breakers and #10 to 30 amp and # 14 to 15amp?? Im speaking of the 75 degree column of course.![]()
Because of Fourier heat transfer calculations and the more complicated Neher-McGrath calculations.
However, some routinely exceed the limited values in some cases. (Normally where they believe 240.4G flatly supersedes 240.4D - not the case IMO.)