I am working on learning to solve Example D(1)(a).
When I look at 210.11(C)(1), it requires at least two 20 Amp. small appliance branch circuits. If I then calculate the capacity of each of these circuits, at 120 V, I obtain: 20 A x 120 V = 2400 VA
Then, 220.52(A) requires the load on those circuits to be 1500 VA each. This gives: 1500 VA / 120 V = 12.5 A
If I interpret these results correctly, the branch circuit conductors are rated to carry a 20-Ampere load but the actual maximum load that will be imposed on them is only 12.5 A. Am I correct?