Why is the derating of conductors for "more than 3" not applicable within a metal wireway up to 30 conductors in the cross sectional area (2017 NEC 376.22(A),(B)), when in all other wiring methods the "more than 3" would become a consideration, even in NM wireways (378.22)?
376.22(B) Adjustment Factors.
The adjustment factors in 310.15(B)(3)(a) shall be applied only where the number of current-carrying conductors, including neutral conductors classified as current-carrying under the provisions of 310.15(B)(5), exceeds 30 at any cross section of the wireway.
378.22 Number of Conductors.
........
The adjustment factors specified in 310.15(B)(3)(a) shall be applicable to the current-carrying conductors up to and including the 20 percent fill specified in the first paragraph of this section.