Why 5 ohms ground resistance?

Merry Christmas
Status
Not open for further replies.

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
I have a new water pumping station that specified 5 ohms ground resistance for the grounding system, with a ground ring, ground rods, and a Lyncote chemical ground rod, and a ufer ground.

The
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Why 5 ohms ground resistance?

Ok if it is specified and using all the electrodes you listed, there should not be much of a problem achieving 5 ohms. Sounds like a telephone office spec to me, at least those are methods I have used to get 5 or less. Did you mean Lyncole?

[ January 14, 2004, 04:06 PM: Message edited by: dereckbc ]
 