Spa & hot tub connections, 680.42(A)(1) states you cant use more than 6' of LFMC or LFNMC.
Requirements for LFNC-B, 356.30(2) "or installed in lengths not exceeding 6' from a luminaire".
Requirements for FMC, 348.20(A)(2) "in lengths not in excess of 6'."
Why is 6' the cut off length I keep seeing throughout the code? I know I have run more than 6' of LFNMC to connect a hot tub before. Whats the correct way to install it so I don't end up running 15' of LFNMC, run EMT or RNMC until I reach the 6' mark and then make the transition to LFNMC to the hot tub connection? Thanks
Requirements for LFNC-B, 356.30(2) "or installed in lengths not exceeding 6' from a luminaire".
Requirements for FMC, 348.20(A)(2) "in lengths not in excess of 6'."
Why is 6' the cut off length I keep seeing throughout the code? I know I have run more than 6' of LFNMC to connect a hot tub before. Whats the correct way to install it so I don't end up running 15' of LFNMC, run EMT or RNMC until I reach the 6' mark and then make the transition to LFNMC to the hot tub connection? Thanks