Why are you allowed to put multiple egc's together in one hole that is clearly identified for 1 conductor on typical ground bars ?
there is no such exception.ok. I meant neutral bus bar or ground bar really. But, obviously their ports are round and appear UL listed for 1 conductor. Is there an exception somewhere that states if it doesn't normally carry current you can put in as many as fits ? It's done here all the time and it always passes
Why are you allowed to put multiple egc's together in one hole that is clearly identified for 1 conductor on typical ground bars ?
Which probably has more to do with NEC not allowing more then one conductor per hole for the grounded conductor then whether or not the hole is listed for more then one conductor.It was explained to me (by Fred Hartwell!) that neutral wires, being current-carrying conductors, will warm up under use and if they warm unevenly due to differing loads, then when sharing a slot the connection may loosen over time because of uneven expansion and contraction of the copper.
Equipment grounding conductors, which are not current-carrying, will not have the same effect. So if the panel allows, grounds can be grouped , or paired, in one hole.
Read the instructions for the panel. In most cases the bar is listed for 2 or 3 EGCs per hole and one grounded conductor.ok. I meant neutral bus bar or ground bar really. But, obviously their ports are round and appear UL listed for 1 conductor. Is there an exception somewhere that states if it doesn't normally carry current you can put in as many as fits ? It's done here all the time and it always passes
Read the instructions for the panel. In most cases the bar is listed for 2 or 3 EGCs per hole and one grounded conductor.