ptonsparky
Tom
- Occupation
- EC - retired
View attachment 10880
This MWBC fed some old K&T and has worked for some years. Individual 15 amp CBs installed as was the custom before enligtenment.
New shingles went on recently and vibration of work caused center post of lampholder in attic to shortcircuit to shell. Not sure how many times the renters reset the CB before they noticed smoke and melting of the cable near the panel.
We, my help, modified the wiring so a new model of CH AFCI has been installed. K&T is still a factor but MWBC is not, as we refed with a single circuit. Taps from somewhere to someplace may be a problem but he was supposed to have checked for those.
Two hours after he left we get the call that the AFCI had tripped. Stay tuned for hourly updates...