mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
Why aren't potential voltage transformers fused? Am I correct there is no requirement in the NEC or NESC?
Yeah, I agree, VTs are always fused, CTs are NEVER fused.
Only time I see unfused PTs are at transmission levels.
(C) Voltage (Potential) Transformers. Voltage (potential)
transformers installed indoors or enclosed shall be protected
with primary fuses.
Informational Note: For protection of instrument circuits
including voltage transformers, see 408.52.
Two things come to mind:Ok, got found this in the NEC at 450.3 (C):
So anything outdoor in the open can be unfused. But my question is why would the NEC allow this?
I don't know what your code requirements are but I've always fused them.Why aren't potential voltage transformers fused? Am I correct there is no requirement in the NEC or NESC?
Two things come to mind:
1. POCO equipment is not covered by the NEC, and
2. An overloaded PT outside in the open is not likely to start any fires or be an injury hazard. Like secondary wires on a service transformer, it will just burn out and stop the fault current that way.
For outdoor use the VT is liable to be a capacitive voltage divider. As for fuses, look at the size of them.
At what side? High or low side of vt?
Low side always have protection on it, as for the high side, we can rely on the protection of the line for that matter.
Maybe you dont see fuses because they are breakers.. Hahaha
Sent from Mars
Have seen folks bypass PT fuse on big gensets because they forgot to set the system up to disconnect voltage reg when the engine is shutoff. Voltage stays up while frequency drops, saturates PT and blows fuse and they cannot figure out why th;e fuse blows so they just bypass it !
The high side, low side always has fused protection.
If the vts are directly connected to the bus, then, the protection lies of the line protective relays.. If the connection uses a string of conductors normally it has fuse cut outs.