mark32
Senior Member
- Location
- Currently in NJ
I hooked up a ceiling light and installed a used (From the owner) dimmer the other day for someone. I confidently told the owner to flip the breaker back on fully expecting the light to come on. When it didn't light up I asked him to change the bulb, which did nothing but noticed the locator light in the dimmer go off and on when the bulb was removed and installed, just like it's suppoed to. I whipped out my meter but the battery was dead. The owner handed me a his tester, the 120v or 240v type with two leads. The 120v light in the tester lit up when I tested at the light's socket. I couldn't understand what the problem could be. The owner said he had shorted one of the leads of the dimmer when he initially installed it and then told me the light hadn't worked since. I removed the dimmer and touched the feed and sw leg together and the light came on. My question is why would the locator light light up and why would I get a voltage reading at the light socket when the light still would not work?