Re: Why disconnect switch to be preffered overCircuit breake
The main reason for safety disconnects in sight of a motor-driven unit is for emergency shutdown or as a lock-out device for service work. Some industries are more severe in their requirements than others. The reason the disconnect should be mounted within sight of the unit & labeled properly is so that the correct device has power removed. My industry is governed by MSHA - and as such "visible" disconnects are required when doing electrical service - a circuit breaker by design does not provide "visible" indication that the power connections are severed - thus an electrician must verify with a volt-meter that the motor leads are de-energized. I only use disconnects with a viewing window, thus a non "electrical" person can do mechanical maintenance without the need for an electrician to be present. Stop switches & pull-cords are not acceptable lock-out devices for doing service work as wiring shorts or faulty switches (or PLC forces)can allow machines to re-start, hence the need for a local lock-out device that prevents motor starting. In most of our surface facilities the MCC room with the MCP devices is not close to the actual device, sometimes 4-5 floors and hundreds of feet away.