why do wires melt in junction box

Status
Not open for further replies.

ddk2b408

Member
at a job power went out in the living room so I thought maybe a breaker tripped. breaker was fine, I pulled all outlets in room out the wall, wiring was fine. I traced circuit to a junction box. Wires were burned and came apart. Why breaker didnt trip. and what causes a wire to melt that way. by the way It was a 12/3 so the circuit was sharing a neutral...
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
You didn't happen to take any pictures of it, did you?

Bad connections generate heat, among other things that do too. I've seen loose connections at breakers melt the sheathing tag onto the conductors in a big glob.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Poor connections create heat, but also limit the load so it is unlikely that the breaker will trip. Just look at things like toasters...they make a lot of heat but the breaker does not trip. This is one of the classic cases used to support the AFCI requirement. I am not yet convinced that the fancy arc signature recognition chip in the AFCI will see a poor connection, but all AFCIs have GFPs and it does not take long for a high heat condition to create a low level ground fault that will cause the AFCI to trip.
Don
 

Inspectorcliff

Senior Member
Location
Colorado
not good.

not good.

:confused:
ddk2b408 said:
at a job power went out in the living room so I thought maybe a breaker tripped. breaker was fine, I pulled all outlets in room out the wall, wiring was fine. I traced circuit to a junction box. Wires were burned and came apart. Why breaker didnt trip. and what causes a wire to melt that way. by the way It was a 12/3 so the circuit was sharing a neutral...
As already stated, Two items that creat this, 1) heat and 2) overloading the circuit. BUT, not a dead short. I have seen a number of these over the years.:roll:
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I really doubt that having two hots of the same phase on a common neutral would really make enough heat to melt the insulation. Remember that the conductors in the NM are rated at 90?C and #12 has an ampacity of 30 amps at this temperature rating. Yes it is a code violation and will contribute to heat build up, I don't think that alone would result in melting.
Don
 

lpelectric

Senior Member
ddk2b408 said:
at a job power went out in the living room so I thought maybe a breaker tripped. breaker was fine, I pulled all outlets in room out the wall, wiring was fine. I traced circuit to a junction box. Wires were burned and came apart. Why breaker didnt trip. and what causes a wire to melt that way. by the way It was a 12/3 so the circuit was sharing a neutral...

Were they Federal Pacific breakers? :confused:
 

goindowner

Member
Location
Tallahassee.Fl
--------------------------------------------------------------------------------

Poor connections create heat, but also limit the load so it is unlikely that the breaker will trip. Just look at things like toasters...they make a lot of heat but the breaker does not trip. This is one of the classic cases used to support the AFCI requirement. I am not yet convinced that the fancy arc signature recognition chip in the AFCI will see a poor connection, but all AFCIs have GFPs and it does not take long for a high heat condition to create a low level ground fault that will cause the AFCI to trip.
Don







I helped a friend wire his new house a few years ago. He and his brother inlaw put the recpts in the bedrooms. I could not figure out why one afci was tripping. We changed the breaker with one that was not having any problems to make sure we did not get another bad breaker. Problem still was happpening. We then took out every recpt. in this one particular bedroom and found the guy did not tighten the screws good. Problem solved.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Problem still was happpening. We then took out every recpt. in this one particular bedroom and found the guy did not tighten the screws good. Problem solved.

Loose connections are a serious problem, but I really doubt that the current generation of branch-circuit feeder type AFCI breakers would trip due to the loose connection as Don has already pointed out. It is more likely that there was an inadvertant neutral to ground connection in one of the receptacle boxes that resulted in the AFCI breaker tripping. The standard branch-circuit feeder type of AFCI breaker also has GFPE protection which will trip at between 30 and 50 milliamps.

Chris
 

andinator

Senior Member
Location
Lilburn Georgia
I saw a beauty this morning---One of the guys I work with brought the mess in for show and tell in a plastic baggie. 1 #4 cu stranded and 1#6cu stranded= meltdown.:cool:
 

celtic

Senior Member
Location
NJ
don_resqcapt19 said:
I really doubt that having two hots of the same phase on a common neutral would really make enough heat to melt the insulation. Remember that the conductors in the NM are rated at 90?C and #12 has an ampacity of 30 amps at this temperature rating. Yes it is a code violation and will contribute to heat build up, I don't think that alone would result in melting.
Don

I must disagree.
I have personally seen 12/3 NM baked (neutral only if I recall) as a result of both ungrounded conductors being on the same phase. We had an entire panel running temp. lighting stringers, "someone" liked the "all black one side, all red the other side" appearance. It took about a year for the charring on the sheath to become visible OUTSIDE the panel.

Another job I wish I had a camera with me....
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Celtic,
Unless you are running more than 15 amps of each ungrounded conductor, the grounded conductor would be operating at or below its rated 90C ampacity. If this is causing the insulation to fail, then it isn't really 90C insulation.
Don
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
weressl said:
More importantly, I do not believe this issue belongs to the Hazardous Area Classification group.
Good point. I have moved it to the Safety Topic Area.
 

LawnGuyLandSparky

Senior Member
celtic said:
were they on the same phase?

Did some work for a furniture store where miles of 2-circuit track was added by the previous tenant (also a furniture store.) Every track had both hots landed on the same phase via piggyback breaker, ALL of the neutrals were either dark yellow or brown. And this was THHN in EMT.
 