Coppersmith
Senior Member
- Location
- Tampa, FL, USA
- Occupation
- Electrical Contractor
According to table C.1 I can run five #2 XHHW conductors in 1.25" EMT. I bought a 1.25" T conduit body and it says inside "Max three #2". What gives?
They also make tees that are open on the back that are more forgiving on wire fill.not sure about tees but for an LB they make a 'mogul LB' which is long enough to meet the bend radius rules and you can fill to the max conduit fill
According to table C.1 I can run five #2 XHHW conductors in 1.25" EMT. I bought a 1.25" T conduit body and it says inside "Max three #2". What gives?