Therealcrt
Senior Member
- Location
- Kansas City
- Occupation
- Electrician
I’m doing some troubleshooting on some parking lot pole lights there are two circuits sharing one neutral going out from the contactor cabinet to the pole light. I disconnected all of the incoming wires to the pole, separating everything when I turn the circuits on and cover the photocell to close the contactor. It blows the contactor and keeps the contactor in a stuck closed position. I’ve replaced two contractors now there is no continuity between any hot and ground or any hot and neutral or any hot and hot when I have one circuit on it holds the breaker, but when both circuits are on it trips, both breakers Again there is no load connected no indicator of a short or fault it’s 277 V to add And the contactor is a three pole 30 amp 277 V coil contactor. The breakers are single pole 20 amp breakers.