GBMorris
Member
- Location
- Regina, SK, Canada
Hi Folks,
Why is it common practice to ground (earth) the ground terminal in split-phase residential service? I fully understand the reason for the ground wire connection to the enclosures of appliances, etc., however, it is not clear why this ground wire must actually be "grounded" or "earthed". In what way would it not be feasible for the entire 120/240V circuit to be floating with respect to earth?
I do not know the answer, but I do not believe arguments around safety or GFCI operation hold water:
It does not seem that a grounded system is more safe, since in a grounded system there is a path for the current to return to the source through an earthed person. This is not the case with a floating circuit?if the person is the only part of the system that contacts earth, no current will flow through them.
The GFCI system can operate regardless of ground potential, since it only detects a discrepancy in the currents on the hot and neutral conductors and has nothing to do with voltage. Whether the faulty current path is through ground or elsewhere is irrelevant.
A colleague and I have been struggling with this question. Any insight you can provide would be appreciated!
For background, I am a transmission P&C engineer with a masters degree in electrical engineering, and about four years of experience.
Thanks!
Greg
Why is it common practice to ground (earth) the ground terminal in split-phase residential service? I fully understand the reason for the ground wire connection to the enclosures of appliances, etc., however, it is not clear why this ground wire must actually be "grounded" or "earthed". In what way would it not be feasible for the entire 120/240V circuit to be floating with respect to earth?
I do not know the answer, but I do not believe arguments around safety or GFCI operation hold water:
It does not seem that a grounded system is more safe, since in a grounded system there is a path for the current to return to the source through an earthed person. This is not the case with a floating circuit?if the person is the only part of the system that contacts earth, no current will flow through them.
The GFCI system can operate regardless of ground potential, since it only detects a discrepancy in the currents on the hot and neutral conductors and has nothing to do with voltage. Whether the faulty current path is through ground or elsewhere is irrelevant.
A colleague and I have been struggling with this question. Any insight you can provide would be appreciated!
For background, I am a transmission P&C engineer with a masters degree in electrical engineering, and about four years of experience.
Thanks!
Greg