11Haze29
Member
- Location
- Rhode Island
- Occupation
- Electrical Engineer
I know its required, but what is the actual purpose. The utility brings both hots and a neutral to the service panel. They also ground the neutral at the pole with a solid #6 and a ground rod. So by grounding the neutral bar in the service panel, you effectively create a two paths for the neutral current to return to the transformer. One is the neutral conductor, but the other is the earth. Granted the neutral is the low resistance path, but the earth path is still in parallel. So if we had a hypothetical neutral current of 10 amps in our 240/120 single phase service panel, and the neutral cable to the transformer has 0.5 ohms resistance, and the earth path is 25 ohms, then the neutral is carrying 9.8 amps and 0.2 amps is flowing through the earth ground. You probably read the stories about cows being shocked on the farm, and flowing ground current is the culprit.
So in theory, you would NOT want current flowing through the earth. I've heard from fellow electricians that the reason is to act as a 'safety' in case the neutral service cable ever became disconnected. Higher voltages than 120 could develop on line to neutral loads, possibly causing a short or fire. So the neutral being grounded to the earth provide another path that will keep voltages at a reasonable level and also permit single pole breakers to continue to operate.
Does anyone have a better explanation.
So in theory, you would NOT want current flowing through the earth. I've heard from fellow electricians that the reason is to act as a 'safety' in case the neutral service cable ever became disconnected. Higher voltages than 120 could develop on line to neutral loads, possibly causing a short or fire. So the neutral being grounded to the earth provide another path that will keep voltages at a reasonable level and also permit single pole breakers to continue to operate.
Does anyone have a better explanation.