I have a tenant improvement project located in a recently build, half-rented, multi- unit shopping center.

I submitted a set of plan for plan check
after days, the plan checker commented that I need to comply with 220-87 on the existing 2000A multimeter service.

What should I do????
the shopping center is 40% full with tenants.

Thank you
:happysad:
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
220.87 exception:
"The recording shall reflect the maximum demand of the feeder or service by being taken when the building or space is occupied.."

Your 40% occupancy is measured for 30 days, submitted under 220.87, and the remaining 60% of service is extrapolated for future expansion;
90.1(B) - Exempt from NEC
90.8(A) - Wiring Planning

If AHJ demands sizing service Mains OCP for current 40% occupancy, you could attach a change order to such AHJ orders. Needed for adding smaller breakers that fit same gear, and Service-call costs when higher occupancy trips Mains and larger breakers are required. The change order can direct all tenant law suits for power-loss damage to the responsible planning department, and document your objections.
 