cowdr4
Member
- Location
- Pomona, IL, USA
Why is a sub*panel not "effectively" bonded when connected to main panel by emt?
Specific situation: 200 amp main service panel with bonded neutral bar and ufer ground. Main panel has 100 amp 240V breaker feeding 2 #3 Cu wires that are connected to 100 amp main disconnect of 100 amp sub-panel. Additional #3 Cu wire connecting sub-panel and main service panel neutral bars and a #6 bare Cu wire connecting sub-panel ground to neutral bonded bar in main 200 amp panel. Sub-panel is approximately 3 feet from main panel, and is connected by EMT conduit. Sub-panel neutral bar is not bonded to panel chassis with a bonding screw.
All of the above meets NEC, but even without the bonding screw, isn't the sub-panel effectively bonded to the chassis via 2 separate paths? The EMT conduit between the main and sub-panel provides a direct path for electricity from the sub-panel neutral to main panel neutral via the neutral wire, then to the main panel chassis via bonding screw, then to EMT, and finally to sub-panel chassis. Additionally, the bare Cu ground can provide a direct path for current from sub-panel neutral to the chassis by contacting either the chassis or EMT directly. Why is a 1/4 inch path through a bonding screw an issue when neither of the above 3-6 foot long pathways appear to be a concern? Thanks!
Specific situation: 200 amp main service panel with bonded neutral bar and ufer ground. Main panel has 100 amp 240V breaker feeding 2 #3 Cu wires that are connected to 100 amp main disconnect of 100 amp sub-panel. Additional #3 Cu wire connecting sub-panel and main service panel neutral bars and a #6 bare Cu wire connecting sub-panel ground to neutral bonded bar in main 200 amp panel. Sub-panel is approximately 3 feet from main panel, and is connected by EMT conduit. Sub-panel neutral bar is not bonded to panel chassis with a bonding screw.
All of the above meets NEC, but even without the bonding screw, isn't the sub-panel effectively bonded to the chassis via 2 separate paths? The EMT conduit between the main and sub-panel provides a direct path for electricity from the sub-panel neutral to main panel neutral via the neutral wire, then to the main panel chassis via bonding screw, then to EMT, and finally to sub-panel chassis. Additionally, the bare Cu ground can provide a direct path for current from sub-panel neutral to the chassis by contacting either the chassis or EMT directly. Why is a 1/4 inch path through a bonding screw an issue when neither of the above 3-6 foot long pathways appear to be a concern? Thanks!