Um....................I'm British.
I just use the FLC from the nameplate.
We are not permitted to do that under the rules of the NEC.
[/quote]430.22 Single Motor.
Conductors that supply a single motor used in a continuous duty application shall have an ampacity of not less than 125 percent of the motor full-load current rating, as determined by
430.6(A)(1) ....
430.6(A)(1) Table Values.
Other than for motors built for low speeds (less than 1200 RPM) or high torques, and for multispeed motors, the values given in Table 430.247, Table 430.248, Table 430.249, and Table 430.250 shall be used to determine the ampacity of conductors or ampere ratings of switches, branch-circuit short-circuit and ground-fault protection, instead of the actual current rating marked on the motor nameplate. ....[/quote]