Why is it usually the neutral?
Twoskinsoneman
West Virginia, USA NEC: 2020
Facility Senior Electrician
I was going to replace the plug on this extension cord. I found the grounded conductor a bit burnt. It got me thinking. Whenever I find this exact situation, which I have several times, it's always the grounded conductor. Is there an electrical reason?
By any chance did you strip the white insulation back at least an inch and inspect that area. During my 50 enjoyable years as a commercial electrician have found copper cord strands discolored. Only time they were burnt was at a poor connection on a device. Recently converted one of my 4' garage luminares to LED. When I removed the ballast cut back the quality yellow 16/3 Bronco cord that I installed over 45 years ago. Was going to replace it but copper strands were still bright and insulation pliable so did not replace the cord. Color on cheap SJO ( believe only rated for 300 volts) copper strands were often discolored entire length on installs maybe over 10 years.
In a two wire circuits there is no reason why one conductor should be different than the other from use. My guess is that they're not burnt they were just manufactured that way with discolored strands.
That kinda brings up another can of worms, why do the neutral on buried cables fail way more than the hots? Maybe pinhole lightning damage? Water intrusion because of that? There should be very little, if no voltage leakage because it’s at the relatively same potential as earth.
I have repaired lots of underground, almost always is an ungrounded conductor that I have repaired unless someone physically did some damage, like with excavating equipment or driving a post or similar item into it.
Occasionally have had a failing ungrounded conductor cause heat damage to insulation on adjacent conductors though. Had one of those just a couple weeks ago.
I’ve had the opposite experience, almost always the grounded conductor in direct burial cable. Now in conduit, it’s always the ungrounded conductor.
Copper, aluminum, either?
Most the underground failures outside of physically damaged items I run into is usually direct bury aluminum conductors and most the time is an ungrounded conductor that had failed. Likely due to abrasions while handling is my guess on a majority of them. Rodent damage can be either but there is usually nearby evidence of rodent activity to help determine when that is the cause. Still amazes me to see 277 volt to ground conductors but never any dead rodents involved. My guess is they only use their teeth and they are of high enough quality of an insulator that they get away with it.
Unlike many claims, they don't eat this insulation, they are shredding it and gathering it to use for nesting material, so taste of it is not a factor.
Yeah. I was hoping the cord could be salvaged. I cut back a foot, then 5 feet. After deciding to junk it I even cut into near mid way out of curiosity. IMHO the grounded conductor looks overheated throughout.
Perhaps. I've never seen new cord with one conductor that looks like that but I haven't seen it all. I do feel like I can tell when copper has been overheated. Beside the blackening and duller color you can see in the pic, when I fan out the individual strands and flatten it, it has the darker red color that's always indicated to me excessive heat.
Just a wild guess but wonder if the coloring agent or dye they use to produce white insulation has an effect on the copper. Black insulation might use common lamp black to produce that color. According to a Google search lamp black is very stable & unaffected by light, acids & alkaloids.
Or maybe the white insulation melts at a lower temp.
Could just be nonlinear loads and excess heating from harmonics, though that is just a stab in the dark.
But that only affects multiwire circuits. Thats why you find an oversized neutral on office furniture.
And mostly only the neutral on systems supplied from a wye secondary.
Even when there is a wye source you still have the same current/same harmonics in both receptacle slots of a two wire circuit.