Why is one leg higher than the other?

Merry Christmas
Status
Not open for further replies.

mmas0n

Member
I was looking at a commercial deep fryer and noticed that all the models offered were 208V & and each leg was of equal amps except one, that particular unit listed 2 of the legs at 22 amps and the other at 36 amps. I could not see any glaring differences in the units besides a small size difference. Why would there be such a substantial amp draw difference on 1 leg compared to the other two?
 
I was looking at a commercial deep fryer and noticed that all the models offered were 208V & and each leg was of equal amps except one, that particular unit listed 2 of the legs at 22 amps and the other at 36 amps. I could not see any glaring differences in the units besides a small size difference. Why would there be such a substantial amp draw difference on 1 leg compared to the other two?

Just a guess, but it sounds like there is a line to neutral load and that one leg is carrying that load.
 
Just a guess, but it sounds like there is a line to neutral load and that one leg is carrying that load.

I suppose it could be the electronic controller for the fryer, but I can't imagine any controller sucking up 15 amps.
 
I suppose it could be the electronic controller for the fryer, but I can't imagine any controller sucking up 15 amps.

They may have needed to use a combination of individual heating elements that would not allow them to balance the load precisely. (For example, 7 resistance heating elements do not divide evenly by three.)
 
Sounds to me like they have a unit with two heating elements. For single phase the elements would be paralleled. For "three phase" one element would be connected A-B and the other B-C. Phases A and C would each see one element but phase B would see both. Because of phase shift the load on B is about 1.7 X the load of a single element.
 
Sounds to me like they have a unit with two heating elements. For single phase the elements would be paralleled. For "three phase" one element would be connected A-B and the other B-C. Phases A and C would each see one element but phase B would see both. Because of phase shift the load on B is about 1.7 X the load of a single element.
I'm leaning this way myself. 22A x sqrt(3) = 38A. The nameplate (or spec's) say 36, so there could be a small load across the otherwise open end of the delta configuration... or if 4-wire, some 120V load on the uncommon 208 lines.
 