Originally posted by syakoban:
If they are the same gage wire, is it the fact that there are other metallic devices connected to the ground that lowers impedance? How would that work with plastic boxes?
When plastic boxes are used, and say, NM-B cable, and there is only one receptacle on the whole circuit, then you are absolutely right. . .the impedance of the ground is the same as the impedance of the other two wires, when the cables are #14, #12 & #10. With #8 NM-B, the ground will be #10 and the ground impedance will actually be
greater than the insulated conductors.
Now, think of a kitchen counter. Imagine, at the right side of the sink on the back splash of the counter, there is a 3 gang box holding two switches and a small appliance counter receptacle. One switch controls the light over the sink and is on a lighting circuit. The other switch controls the disposal which is on its own 15 Amp 120 Volt circuit. The receptacle is supplied by a 20 Amp 120 Volt small appliance branch circuit.
The ground wires in the 3 gang box are all tied together per 2005 NEC 250.148. If one of the hot wires in the 3 gang box faults to a ground in that box, the fault current will travel back on two #14s and the #12 ground wires in parallel.
The interconnection of the grounds in the 3 gang box lowers the impedance of the ground below the individual ground wire impedances.
The more interconnections of parallel grounds, the lower the overall ground impedance.