TM519
Member
- Location
- United States
According to NFPA 70 (NEC) 490.71, for an Electrode-Type Boiler it states that it must only be supplied from a 3-phase, 4-wire solidly grounded wye system, or from isolating transformers arranged to provide such a system. What I have been unsuccessful in finding out is why for an electrode-type boiler is there the specific requirement for the grounding to be a solid ground?
We are installing an electrode boiler on a 6.9kV 3-wire system, so we need to implement a 4-wire solution in order to ground the boiler. This can be done with an isolation transformer and solidly grounding the secondary side.
With other equipment that do not say to exclusively use a solidly grounded system, another option would be to install an NGR with a zig-zag transformer, which accomplishes the same thing, at a significantly cheaper price.
We will be installing an Isolation Transformer in order to achieve a solidly grounded system to meet NEC, but I would just like to know why the specific requirement for an Electrode-Type Boiler to be solidly grounded? I have an electrical background, but I don't know much about Electrode-Type Boilers other than the basics of how they work.
We are installing an electrode boiler on a 6.9kV 3-wire system, so we need to implement a 4-wire solution in order to ground the boiler. This can be done with an isolation transformer and solidly grounding the secondary side.
With other equipment that do not say to exclusively use a solidly grounded system, another option would be to install an NGR with a zig-zag transformer, which accomplishes the same thing, at a significantly cheaper price.
We will be installing an Isolation Transformer in order to achieve a solidly grounded system to meet NEC, but I would just like to know why the specific requirement for an Electrode-Type Boiler to be solidly grounded? I have an electrical background, but I don't know much about Electrode-Type Boilers other than the basics of how they work.