208 Volt 3phase HVAC Condensor keeps "melting" the breaker! Actually it looks more like it is arcing at the breaker/phase bar contacts until the plastic heats up & crumbles away. (3RD time now!)
First time the breaker lasted 1-2 years, now they only last about 2-3 months!
Unit Specs:
Min Cir Amps: 43
Max HACR Breaker: 50
It's wired with #6 THHN on a 3-pole 50 amp breaker. Maybe 25' run, if that.
Each of the 3 legs are pulling around 31 amps.
HVAC guy checked out the unit, said it was fine. I cleaned off the phase bar (It was actually still in great shape) put a new 3-pole breaker in, unit works fine again...for about 2 months! Then I get another call... it happened again!
The breaker is Very warm to the touch after only 15 minutes of use.
I confirmed the unit is 208 according to the spec. sheet on the unit.
I called the manufacturer...got the run-around... "you need to call the distributor", so I called the distributor, "you need to call the manufacturer"...
Any suggestions?
Dave
First time the breaker lasted 1-2 years, now they only last about 2-3 months!
Unit Specs:
Min Cir Amps: 43
Max HACR Breaker: 50
It's wired with #6 THHN on a 3-pole 50 amp breaker. Maybe 25' run, if that.
Each of the 3 legs are pulling around 31 amps.
HVAC guy checked out the unit, said it was fine. I cleaned off the phase bar (It was actually still in great shape) put a new 3-pole breaker in, unit works fine again...for about 2 months! Then I get another call... it happened again!
The breaker is Very warm to the touch after only 15 minutes of use.
I confirmed the unit is 208 according to the spec. sheet on the unit.
I called the manufacturer...got the run-around... "you need to call the distributor", so I called the distributor, "you need to call the manufacturer"...
Any suggestions?