Am I missing something???
392.80(A)(2)(a)
600MCM or larger, single or grouped...
I plan on using ventilated covers.
Would we simply interpret the implicit omission of ventilated covers as equivalent to uncovered and no need to consider? Just use the 75% free-air rating?
392.80(A)(2)(a)
600MCM or larger, single or grouped...
- You can install cable in tray at 75% free-air current rating in uncovered tray.
- You can install cable in tray at 70% free-air current rating if covered more than 6' with "SOLID UNVENTILATED covers". It is very specific to unventilated covers.
I plan on using ventilated covers.
Would we simply interpret the implicit omission of ventilated covers as equivalent to uncovered and no need to consider? Just use the 75% free-air rating?