Hello,
NEC does not allow splicing ground rod conductors according to 250.64.
Curious if anyone can figure out the reason behind the rule.
The only explanation I can think of is that lightning strikes might damage splices.
Just trying to expand my understanding ...
Thanks!
NEC does not allow splicing ground rod conductors according to 250.64.
Curious if anyone can figure out the reason behind the rule.
The only explanation I can think of is that lightning strikes might damage splices.
Just trying to expand my understanding ...
Thanks!
250.6: [...] grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint. If necessary, splices or connections shall be made as permitted in (1) through (4):
(1) Splicing of the wire-type grounding electrode conductor shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.