You need to check Art 225.30 in regard to the number of circuits and 250.32 reference grounding.
This statement by augie47 got me thinking about the concept behind the rule.
II. More Than One Building or Other Structure
225.30 Number of Supplies. Where more than one building
or other structure is on the same property and under
single management, each additional building or other structure
that is served by a branch circuit or feeder on the load
side of the service disconnecting means shall be supplied
by only one feeder or branch circuit unless permitted in
225.30(A) through (E). For the purpose of this section, a
multiwire branch circuit shall be considered a single circuit.
My question is why? Let's say you've got one BC already going out to separate building and you decide you'd like one more...
Where is the hazard?