At the service why is only one path to ground allowed? What is the reasoning for this?
Yes you can.SmithBuilt said:I could not run the neutral. . .and emt between the meter can and the mdp.
And the commentary following 250.6(D) is:An increase in the use of electronic controls and computer equipment, which are sensitive to stray currents, has caused installation designers to look for ways to isolate electronic equipment from the effects of such stray circulating currents. Circulating currents on equipment grounding conductors, metal raceways, and building steel develop potential differences between ground and the neutral of electronic equipment.
A solution often recommended by inexperienced individuals is to isolate the electronic equipment from all other power equipment by disconnecting it from the power equipment ground. In this ill-conceived corrective action, the equipment grounding means is removed or nonmetallic spacers are installed in the metallic raceway system. The electronic equipment is then grounded to an earth ground isolated from the common power system ground. Isolating equipment in this manner creates a potential difference that is a shock hazard. The error is compounded because such isolation does not establish a low-impedance ground-fault return path to the power source, which is necessary to actuate the overcurrent protection device. Section 250.6(B) is not intended to allow disconnection of all power grounding connections to the electronic equipment. See also the commentary following 250.6(D).
Section 250.6(D) indicates that currents that result in noise or data errors in electronic equipment are not considered to be the objectionable currents referred to in 250.6, which limits the alterations permitted by 250.6(C). See 250.96(B) and 250.146(D) for requirements that provide safe bonding and grounding methods to minimize noise and data errors.