Whats the reasoning on the GFPE on 1KA solidly grounded WYE services and not other configurations.
Thanks.
Thanks.
The handbook states:
"....first required in the 1971 Code because of the unusually high number of burndowns reported on those types of service"
I dont know anything other than that.
From the finding, magnitude of fault current fromgenerator to fault location at the Yn-Yn transformerconfiguration had 26.893 kA. It is higher magnitude ofgenerator current for SLG fault at secondary side of thetransformer than other transformer configurations. In thiscondition, there was a route for zero sequence current toflow in a primary and secondary of the transformer. Themagnitude of SLG fault was similar for Yn-Y, Y-Yn, Y-Y,∆-Y and ∆-∆ configuration, which was 11.283 kA. Thelowest SLG fault from generator to fault location for Yn-∆and Y-∆ configuration was 8.697 kA.