donw said:The only reason I can see to specify a 4-pole ATS over a 3-pole would be distance of the generator from the switch. Is that right?
quogueelectric said:I have noticed that I have only seen the neutrals broken in hospitals.
iwire said:
MIEngineer said:Am I missing something?
quogueelectric said:I dont know if this will help you I am not an engineer but in lets say 35+ years of service I have noticed that I have only seen the neutrals broken in hospitals. This I felt was particularly dangerous to electricians and the reason I noticed it is because it scared me many moons ago. I was testing an ats switch for something and thought that a feeder was dead. I tested all phases to ground first and saw 0 volts. To my surprise when I tested phase to phase I read 480 and this was a 400 amp ast switch I dont remember the exact details but because the neutral was switched the energised Phase conductors had no ground reference until the switch transfered.
I concur I just never thought about it not being the engineer. It makes perfect sense now.iwire said:Any transfer switch that is downstream from equipment ground fault protection should be switching the neutral.
If not you can trip the GFP on a the main.