I must need to revisit some of my old text books.
If there's a Yg-Yg step up transformer from a 3 phase generator where the generator neutral is NOT grounded, if there's a single line to ground fault on the distribution side of the transformer, how is it possible to have over-voltage on the unfaulted distribution phases?
When looking at the zero sequence circuit, I can see how there's the lack of a return to the generator, but I'm having a hard time conceptually grasping how over-voltage can happn since the neutral on the distribution is grounded.
Hypothetical setup is something like this:
(gen)---(Yg)-(Yg)---(dist)
Here's a white paper that is related to this. See Figure 8 and discussion around it.
If there's a Yg-Yg step up transformer from a 3 phase generator where the generator neutral is NOT grounded, if there's a single line to ground fault on the distribution side of the transformer, how is it possible to have over-voltage on the unfaulted distribution phases?
When looking at the zero sequence circuit, I can see how there's the lack of a return to the generator, but I'm having a hard time conceptually grasping how over-voltage can happn since the neutral on the distribution is grounded.
Hypothetical setup is something like this:
(gen)---(Yg)-(Yg)---(dist)
Here's a white paper that is related to this. See Figure 8 and discussion around it.