it's new construction and I added a 10kW electric heat package onto the HVAC install. The total current pull during operation is 41.5amps. That's the motor and the coils. One unit is in the basement and the other is in the attic. I will only be using this heating, obviously, in the winter where the temp in the attic is not 75 or 90 degrees C. The NEC code will not allow me to run 8awg, NM-B to these units but rather it needs to be of high temp insulation, such as THHN. I would need to run #6 that is rated for 55amps at 60C rather than the #8 at 40amps. Is this an application where I can since the temps won't get high? Besides, if the insulation is rated for 90C and the copper wires are still copper, why do they derate the NM-B for 60C? I don't see why I would need to go to #6.